Customer has a 208V, 3ph battery charger for their forklift, which pulls 28A. Charger has a short length of 10-4 SO type cord for the branch circuit, which was installed by previous owner of charger. Under Art. 625.2, the forklift is not an Electric Vehicle, but for kicks I'll still use Art. 625.21 for my OCP. Even without Art 625.21, I still think I have to AT LEAST figure 125%.
28*125% = 35A
Art. 240(D) comes into play.
Even though charger will be installed five or so feet from panel, they still want a disconnect installed. *I think I just answered my own question* I think I'll run EMT from panel to 40A disconnect (if 35A can not be found), and then LFMC or LFNC to battery charger. Use #8 for the branch circuit. Gee, that was easy. Thanks for the help.
Roy
28*125% = 35A
Art. 240(D) comes into play.
Even though charger will be installed five or so feet from panel, they still want a disconnect installed. *I think I just answered my own question* I think I'll run EMT from panel to 40A disconnect (if 35A can not be found), and then LFMC or LFNC to battery charger. Use #8 for the branch circuit. Gee, that was easy. Thanks for the help.
Roy