is there any prohibition to supply a branch circuit from one building to another when each has a separate service and there is a fire wall between the two buildings
Take a look at 224.30. Generally speaking, any given building can have power coming into it by only one means. There are exceptions, but only in limited circumstances.
Where are the mains for the 2 buildings ? Are they grouped together ? If not i see a problem
its indoor branch circuits not outside
Sounds more like a multi-occupancy building rather than two buildings.yes they are sharing a fire wall