Can I use the following procedure to calculate the load permitted on a 20A branch circuit with lights and receptacle?
1. Add 180VA per receptacle.
2. Add the VA of each light fixture multiplied by 1.25 (for a continuous load).
3. Make sure the result is less than 2400VA. The 2400VA comes from (120V x 20A).
The reason I ask is this isn't how I have done these calculations in the past. I have always just added the VA for each fixture and for each receptacle together and made sure the result was less than 1920VA. The 1920VA comes from (120V x 20A x 0.8).
However, the first method lets me place more load on the branch.
Steve