This thread: http://forums.mikeholt.com/showthread.php?t=163459 and the the one the other day regarding a 120 volt motor starter coil fed from the motor branch circuit has me wondering...
We know what the minimum size could be for a neutral used in a service or for a feeder based on code rules. Assume a branch circuit supplying a piece of equipment with both line to line load(s) and minimal line to neutral load. What would the minimum neutral size be? It would seem obvious that it would have to be a least sized to 250.122 for safety reasons in order to trip the OCPD in the case of a line to neutral short. For example, what if the branch OCPD was was 100 amp and the neutral only needed to be a #14 based on the load, what in the NEC would prevent this?
We know what the minimum size could be for a neutral used in a service or for a feeder based on code rules. Assume a branch circuit supplying a piece of equipment with both line to line load(s) and minimal line to neutral load. What would the minimum neutral size be? It would seem obvious that it would have to be a least sized to 250.122 for safety reasons in order to trip the OCPD in the case of a line to neutral short. For example, what if the branch OCPD was was 100 amp and the neutral only needed to be a #14 based on the load, what in the NEC would prevent this?