All single phase main panels from service I installed had NM cable coming out of cabinet box for branch circuit loads and stapled between walls on studs
However the project I’m working on now is at a lab and have made some branch circuits with EMT and THHN wire inside of conduit.
I was told I could not just enter THHN into main panel with bushings and connector? as I would with an nm cable, NM connector and bushings
If wall one one side of panel and other side of room with EMT makes it difficult to continue EMT all the way to each knockout, would I have to use MC
I ONLY have MC cable in 12 AWG
However the project I’m working on now is at a lab and have made some branch circuits with EMT and THHN wire inside of conduit.
I was told I could not just enter THHN into main panel with bushings and connector? as I would with an nm cable, NM connector and bushings
If wall one one side of panel and other side of room with EMT makes it difficult to continue EMT all the way to each knockout, would I have to use MC
I ONLY have MC cable in 12 AWG