I have been asked to run a circuit that is part of our automatic transfer switch and emergency generator backup. This circuit will contain 6 IT switches that are plugged into 6 uninterrupted power supplies. Each of these UPS are rated at 9.2A maximum load and are suggested to be placed on a 15A breaker. Total load of this circuit would be 55.2A which would size my breaker at 60A for the circuit. My thought is to run 60A wire to the top of a disconnect for each of the six UPS. I would then fuse that disconnect with a 15A fuse. To continue the circuit from each disconnect, I would use one that had multi lugs on the line side. Unfortunately, there is around 250 feet of distance from the furthest UPS to the breaker panel which would require me to use 1/0 wire for the branch circuit. Is my plan the way to proceed, or should i split the load into multiple circuits? If you have any advice i'd love to hear it. Thanks.