I have a test question that reads no exceptions apply maximum standard size non delay fuse permitted for branch circuit short circuit and ground fault protection for AC motor where given the following: 2 hp- 120 volt single phase, continuous duty, nameplate current rating 22 amps.

Calculations give 72 amp
I chose 80 amps for the protection
The answer sheet said you must go down to 70 in this case
I could not find a reason why to go down in amperage
What is correct?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I have a test question that reads no exceptions apply maximum standard size non delay fuse permitted for branch circuit short circuit and ground fault protection for AC motor where given the following: 2 hp- 120 volt single phase, continuous duty, nameplate current rating 22 amps.

An 80A fuse would be allowed under exception no 1 to Table 430.52.

If "no exceptions apply" then I would say the max size would be 70A.
 

Chuck 1961

Member
Location
Baytown Tx
The right overcurrent protection

The right overcurrent protection

They did use 24 amp as stated in the table
But I understand now after going back and reviewing 430.52(C)1
With no exceptions!
 