Hello,
Can somebody explain when sizing branch circuit conductor size considering temperature correction for a THHN wire, why do we correct the ampacity per 90 C column in 310.15.b.2.a BUT not based on 60 degree C column if the terminal is only rated for 60 degree C. I thought no matter what type of insulation the wire has, if equipment current is 100A or less, we need to go to 310.15.b.16, 60 degree C column to size the wire and de-rate the ampacity using the 60 degree C column for temperature correction at table 310.15.b.2.a.
Greatly appreciated
Jim
Can somebody explain when sizing branch circuit conductor size considering temperature correction for a THHN wire, why do we correct the ampacity per 90 C column in 310.15.b.2.a BUT not based on 60 degree C column if the terminal is only rated for 60 degree C. I thought no matter what type of insulation the wire has, if equipment current is 100A or less, we need to go to 310.15.b.16, 60 degree C column to size the wire and de-rate the ampacity using the 60 degree C column for temperature correction at table 310.15.b.2.a.
Greatly appreciated
Jim