Branch Circuit to Light on Tree

Status
Not open for further replies.

czars

Czars
Location
West Melbourne, FL
Occupation
Florida Certified Electrical Contractor
2008 NEC, Article 225.26 states that trees can't be used to support overhead conductors. However, I can't find a code article that permits or prohibits using a tree to support a branch circuit and an associated outside light. What am I missing?
 
It is in 410.


410.36 Means of Support.
(G) Trees. Outdoor luminaires and associated equipment
shall be permitted to be supported by trees.

FPN No. 1: See 225.26 for restrictions for support of overhead
conductors.

FPN No. 2: See 300.5(D) for protection of conductors.
 