Hello Everyone,
Long time lurker, first time poster here I've got a question for you fine folks regarding a machine design which proposes a branch circuit upstream of the main disconnect.
My other thought would be to have a disconnect on the drop where the maintenance team can get to it easily. Typically we drop power from above (where it could disconnected at the breaker panel) to the OEM's equipment below on the line. We don't often have a disconnect between our drop and the OEM's equipment disconnect.
Thanks for the help!
Long time lurker, first time poster here I've got a question for you fine folks regarding a machine design which proposes a branch circuit upstream of the main disconnect.
- I am reviewing drawings from a machine supplier from Italy for a new project in the US
- The machine will be fed with a 480 drop
- BEFORE the disconnect and lockout means, they have branched off a circuit to power a single leg 220:24vdc power supply
- This supply is used to monitor safety and door switches even with the machine disconnect in the off position
- The 24vdc is rated at 2 amps
- They have signs on the backplane, but I've never been comfortable with any power staying live in an enclosure after the main disconnect is thrown. Does this violate anything related to OSHA or NFPA? They assure me it is UL compliant.
My other thought would be to have a disconnect on the drop where the maintenance team can get to it easily. Typically we drop power from above (where it could disconnected at the breaker panel) to the OEM's equipment below on the line. We don't often have a disconnect between our drop and the OEM's equipment disconnect.
Thanks for the help!