Branch Circuit Voltage Limitations

Status
Not open for further replies.

RasJuugie

New member
Is it permissible to have a 15' street light pole (post top) with ballast and luminaire operating at 480 volts and be complaint with NEC 210.6 (C) & (D). Does this section also applies to highway signs? Your comments/clarifications will be highly appreciated.
 

ryan_618

Senior Member
Re: Branch Circuit Voltage Limitations

210.6(D) does not apply to 480. 210.6(C) applies, but it doesn't address your concern.

In my opinion, what you describe is perfectly fine. :)
 

derf48

Member
Re: Branch Circuit Voltage Limitations

210.6 (D) of the 2005 code applies to circuits not exceeding 600 volts between conductors, which a 480 volt circuit is. A 480 volt luminaire must be not less than a height of 22 ft. on poles and 18 ft on other structures such as tunnels.

If it is truely a sign that is being connected then it is covered by article 600, which has no input voltage limitations. But it requires an electric sign to be listed. If it is simply outline lighting for a sign, then the requirements of chapters 1 to 4 remain in effect and 210.6 still applies.

Fred Bender
 

pierre

Senior Member
Re: Branch Circuit Voltage Limitations

Derf
Sometimes we need to slow down when we read:

210.6
"(D) 600 Volts Between Conductors. Circuits exceeding 277 volts, nominal, to ground and not exceeding 600 volts, nominal, between conductors shall be permitted to supply the following:"

This typically may be a system of 600Y/347.
You can reference 220.5(A) in the '05, or 220.2(A) in the '02

You missed the portion that requires the circuit to exceed 277v to ground, which in most installation, the system/circuit wiring is 480Y/277 volts. So the 480 volts between conductors would generally not fall into subsection (D).
 

derf48

Member
Re: Branch Circuit Voltage Limitations

My simple answer is a 480 volt circuit is not required to be grounded! And since this does not supply a premise wiring system, it is not required to be grounded.

Fred Bender
 

wirenut1980

Senior Member
Location
Plainfield, IN
Re: Branch Circuit Voltage Limitations

My simple answer is a 480 volt circuit is not required to be grounded! And since this does not supply a premise wiring system, it is not required to be grounded.

Fred Bender
If you are talking about operating a 480 V circuit (phase to phase), then yes, no grounded conductor is required (or used), but the fact remains that the potential of an ungrounded conductor in that system to ground is still 277 V and will not fall under 210.6(D).
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Branch Circuit Voltage Limitations

Dave,
If it is an ungrounded system, then Article 100 (Voltage to Ground) tells us that the voltage to ground is the same as the phase to phase voltage.
Don
 