Re: Branch Circuit Voltage Limitations
Derf
Sometimes we need to slow down when we read:
210.6
"(D) 600 Volts Between Conductors. Circuits exceeding 277 volts, nominal, to ground and not exceeding 600 volts, nominal, between conductors shall be permitted to supply the following:"
This typically may be a system of 600Y/347.
You can reference 220.5(A) in the '05, or 220.2(A) in the '02
You missed the portion that requires the circuit to exceed 277v to ground, which in most installation, the system/circuit wiring is 480Y/277 volts. So the 480 volts between conductors would generally not fall into subsection (D).