garydarling
Member
A project I am bidding asks for 480 volt fluorescent lighting, indoors in an industrial workroom at about 35' elevation. The existing 1000w, 480v hibays are being replaced. I am curious about the legality of 480v lighting indoors.
Article 210.6(C) would appear at first glance to govern this installation, except that it is limited to conductors "not exceeding 277 volts, nominal, to ground". The definition of 'Voltage to Ground' in article 100 is, "...for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit". The question would appear to be, is a 480v circuit, with no neutral conductor present, an "ungrounded circuit"? If so, 210.6(D) would then appear to govern, which would prohibit the use of 480 volt lighting indoors. Electricians I posed this question too said 'What about the conduit, it's grounded?' But I don't think a raceway would count as a part of the circuit.
Does the code intend to prohibit 480 volt lighting indoors, or is this a 'too-literal' reading of the code?
Article 210.6(C) would appear at first glance to govern this installation, except that it is limited to conductors "not exceeding 277 volts, nominal, to ground". The definition of 'Voltage to Ground' in article 100 is, "...for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit". The question would appear to be, is a 480v circuit, with no neutral conductor present, an "ungrounded circuit"? If so, 210.6(D) would then appear to govern, which would prohibit the use of 480 volt lighting indoors. Electricians I posed this question too said 'What about the conduit, it's grounded?' But I don't think a raceway would count as a part of the circuit.
Does the code intend to prohibit 480 volt lighting indoors, or is this a 'too-literal' reading of the code?