pdesai_pe

Member
Is it okay to connect two home-run circuits from a single 20A/3Pole, 480V circuit breaker, as long as the load is not exceeding 16Amp for continuous and 20Amp for non-continuous motor loads?
 
Last edited:
as long as the manufacturer lists the breaker lugs for two conductors you can connect directly to the breaker. If not, you could still pigtail off the breaker and splice into both circuits.
 