This is for a project in Ohio, 2017 NEC.
Customer is adding a wash-water holding tank out back of their production facility. The water will be pumped into a tanker truck using a sump pump controlled by a manual motor starter (with overload protection) located at the tank (outdoors). Panel in the building is 208Y/120 3 phase.
At the tank I want to power a 5 HP 3 phase pump (FLC = 16.7A) and a 1A light. Let's assume that the light is a continuous load. By 430.53(B) "If Smallest Rated Motor Protected" I can size the breaker (in the building) at 16.7 * 2.5 = 41.75, next size up is 45A breaker.
To size the conductors, I use 430.24 "Several Motors or a Motor(s) and Other Load(s)" and calculate 16.7 * 1.25 + 1 * 1.25 = 22.125 A. In the conductor table in section 310, #12 Cu THWN is rated for 25 A in the 75°C column. However, because I am powering a non motor load, does 240.4(D) limit me to a 20 A breaker if I use #12 Cu to supply the light? In that case, I could opt for #10 Cu and a 30 A breaker, or if I went to #8 Cu, I would then be free to use the 45 A breaker?
Customer is adding a wash-water holding tank out back of their production facility. The water will be pumped into a tanker truck using a sump pump controlled by a manual motor starter (with overload protection) located at the tank (outdoors). Panel in the building is 208Y/120 3 phase.
At the tank I want to power a 5 HP 3 phase pump (FLC = 16.7A) and a 1A light. Let's assume that the light is a continuous load. By 430.53(B) "If Smallest Rated Motor Protected" I can size the breaker (in the building) at 16.7 * 2.5 = 41.75, next size up is 45A breaker.
To size the conductors, I use 430.24 "Several Motors or a Motor(s) and Other Load(s)" and calculate 16.7 * 1.25 + 1 * 1.25 = 22.125 A. In the conductor table in section 310, #12 Cu THWN is rated for 25 A in the 75°C column. However, because I am powering a non motor load, does 240.4(D) limit me to a 20 A breaker if I use #12 Cu to supply the light? In that case, I could opt for #10 Cu and a 30 A breaker, or if I went to #8 Cu, I would then be free to use the 45 A breaker?