Branch Circuit

Status
Not open for further replies.

Pjm 63

Member
Good Morning,


I read the definition of branch circuit as the conductor between the final over current device and the outlet. Are the wires that daisy chain from outlet to outlet considered the branch circuit ? I have reconfigured some of the wires in a kitchen, However I have not modified the branch circuit from the over current device to the fist outlet. How I see it I have not modified the branch circuit so therefore I do not need to provide AFCI protection. Is my thinking on this correct?
Thanks in advance for any replies.

Peter
 
The daisy chain wires are still between the OCPD and *an* outlet. The branch does not end at the first outlet.

Sent from my XT1585 using Tapatalk
 
Reconfigured? Sounds like you are trying to get around a requirement by using non-NEC wording. Did you add or move any outlets? Note (IMO) to demo one outlet and install a new outlet in another location is adding an outlet... if you added or otherwise used wire that was not there before.
 
I agree with GoldDigger's interpretation. But I am going to invoke "Charlie's Rule" here. The code's definition of "branch circuit" does say "the outlet," and it does not say "an outlet." Rather, it says "the outlet(s)." That tells me that the daisy chain conductors feeding all the outlets are included in the branch circuit.

That said, the question of whether the work you are doing will bring the AFCI requirements into play is a matter of local codes and will be one for the AHJ to answer.
 
Thanks for the info. Not trying to get around any requirements just want to be sure so I meet all requirements. Have a old Zinsco panel. Just wanted to be 100% sure before I move and upgrade panel to provide AFCI protection or install AFCI/GFCI combo outlet to protect branch circuit.
 
the wires that daisy chain extend the BC.

but make sure you know what an outlet is, its not always where you plug in.

install AFCI/GFCI combo outlet
perhaps bad verbiage. you would install a AFCI/GFCI receptacle (which is typically an outlet), but a blank faced AFI/GFI is not and outlet. you might also protect "outlets" using AFI/GFI ocpd's.
 