R robertpitre Member Location houma Occupation building inspector Jun 14, 2024 #1 We’re in the code dose it say that I must put a 15 amp breaker on a 14 gauge wire, and a 12 gauge wire on 20amp breaker?
We’re in the code dose it say that I must put a 15 amp breaker on a 14 gauge wire, and a 12 gauge wire on 20amp breaker?
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Jun 14, 2024 #2 Motor application would change that.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jun 14, 2024 #3 Art. 240
roger Moderator Staff member Location Fl Occupation Retired Electrician Jun 14, 2024 #4 240.4 be sure to pay attention 240.4(G)
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Jun 14, 2024 #5 240.4
R Rick 0920 Senior Member Location Jacksonville, FL Occupation Electrical Instructor Jun 14, 2024 #6 240.4 (D) Small Conductors
R robertpitre Member Location houma Occupation building inspector Jun 16, 2024 #7 Thank you for the advice and help