C CG02 Member Location Corpus Christi, Texas Jun 13, 2016 #1 Does the NEC speak to maximum number of floors in a high rise building that a single branch circuit can serve? If so, where does this occur?
Does the NEC speak to maximum number of floors in a high rise building that a single branch circuit can serve? If so, where does this occur?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jun 13, 2016 #2 No, the nec is silent on that as long as the circuit isn't overloaded. I assume you are talking about house panel circuits?
No, the nec is silent on that as long as the circuit isn't overloaded. I assume you are talking about house panel circuits?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jun 13, 2016 #4 There is no limit as Dennis mentioned. We may have panels in the basement feeding equipment several floors above.
There is no limit as Dennis mentioned. We may have panels in the basement feeding equipment several floors above.
C CG02 Member Location Corpus Christi, Texas Jun 14, 2016 #5 Thanks for your input guys. I appreciate it.