BRANCH CIRCUITS IN THE SAME RACEWAY

Status
Not open for further replies.

sedeca

Member
I WANT TO KNOW IF WE CAN RUN BRANCH CIRCUITS FROM DIFERENT PANELS IN THE SAME RACEWAY.IF THE ANSWER IS YES, WHAT DO WE DO WITH THE EQUIPMENT GROUNDS?

SERGIO DELGADO
NEW HAVEN,CT
 
Re: BRANCH CIRCUITS IN THE SAME RACEWAY

This is only your 2nd post, welcome to the forum. Also, please do not use the Caps Lock feature. It is perceived as shouting and it makes your post difficult to read. :D
 
Re: BRANCH CIRCUITS IN THE SAME RACEWAY

Article 200 does not cover equipment grounding requirements.

At any point you splice the circuit conductors in a box or enclosure, all equipment grounds associated with those circuit conductors should be bonded together.
 