S sj241s Member Dec 12, 2008 #1 this sit has many buildings with two shop buildings next to each other.my questions is can the second shop utilize branch circuits from the first shop or dose it need own panel? and if so can it be feed from shop one as a sub panel.
this sit has many buildings with two shop buildings next to each other.my questions is can the second shop utilize branch circuits from the first shop or dose it need own panel? and if so can it be feed from shop one as a sub panel.
B bphgravity Senior Member Location Florida Dec 12, 2008 #2 Section 225.32 of the NEC gives you some options. Review this section. Also be sure to check out 250.30 while your at it.
Section 225.32 of the NEC gives you some options. Review this section. Also be sure to check out 250.30 while your at it.