A facilties outbuilding requires a 50 amp 480 volt feeder to support a 30 kva transformer and associated low side panel. Since this is a seperate building from the primary building and service there is a disconnect at the outbuilding ahead of the transformer.
The electrical engineer calls out for 4 number 6cu plus appropriate ground and bonds neutral and ground at the disconnect.
Since the transformer does not require a neutral does the code require this be pulled out to the outbuilding?
The electrical engineer calls out for 4 number 6cu plus appropriate ground and bonds neutral and ground at the disconnect.
Since the transformer does not require a neutral does the code require this be pulled out to the outbuilding?