This is a basic overview of a service call I am working on and would like to know if I have overlooked anything. Floor warming mat rated at 360 watts at 120v should have a resistance reading between 31 and 35 has a GFI built into the t-stat. Matt was installed four years ago, shortly after move in day it started tripping GFI on the stat, checked it only with digital meter and found nothing that stood out. Company called the manuf found out that the changed t-stat brand been having trouble with the GFI tripping out so we installed new. We had same problem with new stat so we called tech support again and tried there next suggestion use the stat to control a contactor and feed floor mat with GFI breaker, this seemed to solve the problem last winter. This winter turn the stat on and there is a instant trip of the breaker. I went today and did these test: Turned breaker on with stat off, breaker held engage stat breaker tripped. Checked resistance of matt it read 33. Checked for continuity on branch circuit and floor matt leads everything okay. Bypassed the GFI and took amp readings Hot side 3.4 neutral 3.3, place clamp around both and read zero, check hot read 3.3 and neutral reads 3.4. I did use a megger before taking the amp readings and recorded the following at a 1000v on the branch circuit H/N, H/G, N/G all read greater than 2.2 g ohms ( I believe this is acceptable) on the floor heat cable H/G or N/G read 0 and on the meter it shows only 33 volts in the bottom right hand window (fluke 1587) this leads me to believe there is a nick in the cable. I know this is a long post but I don't want to overlook anything before tile comes out and I don't meg that often and want to be sure of my readings
Thanks