Breaker 1,3,5 used for MCB?

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You are talking about back feeding a breaker. Most panels have a designated spot at the top for a back feed breaker. remember these breakers must have a hold down kit so that determines where it will be in the panel.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You are talking about back feeding a breaker. Most panels have a designated spot at the top for a back feed breaker. remember these breakers must have a hold down kit so that determines where it will be in the panel.
How long has the retention requirement been around?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The back-fed main CB can go anywhere in the panel.
Not on all panels from what I remember. I think GE has a spot near the top for their hold down kit.

They may have changed that because of the solar breakers which are required to be at the bottom.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not on all panels from what I remember. I think GE has a spot near the top for their hold down kit.

They may have changed that because of the solar breakers which are required to be at the bottom.
Sorry I meant code wise there is no limitation for a panel like the one in the OP.
 

norcal

Senior Member
With Cutler-Hammer CH panels the hold down/breaker retainer only works in the upper poles, first required in the early to mid 1990's. Makes it a pain if a main needs to be added to a prior era panel.
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
I had a Eaton BR panel that I mounted a gen interlock on it.

No problem there.

The main was 125 amp with a hold down on it

I ordered a 30 amp to connect the backfeed from a 7kw gen with another hold down kit.

Problem is the smaller breakers do not have the hole in them so you can't put the hold down on it
 

Mr. Serious

Senior Member
Location
Oklahoma, USA
Occupation
Electrical Contractor
Problem is the smaller breakers do not have the hole in them so you can't put the hold down on it
I know this is an old thread, but I wanted to let you know, you can special-order the smaller rated BR breakers with a hole in them for the hold down screw. I think BR260 and above come with it anyway, but for the smaller sizes such as a 30 or 40 amp, you just add a B on the end of the part number. For your 30 amp example, you would need a BR230B instead of a BR230.

The problem is, most suppliers don't carry them, and many suppliers don't distinguish between the BR230B and the BR230 in their inventory, so even though you may order the correct one, it still could show up without the hole, unless you call first, and make absolutely sure that what is pictured on their site is what they are sending you.

It's better if you're working with a panel that is old enough that the old Bryant type BR breakers can legally go in it, because back then they all had holes.
 

GarwoodV6

Member
Location
Houston suburbs
Occupation
30 year commercial Electrician
If the breaker bring installed is backfed from a generator with its own OCP on the output isn't it just a switch? If so, a 60 amp C-H BR CB with the hold down mounting hole could be fed by smaller wiring sized to the OCP on the generator.
The OCP is provided at the source (generator) and the backfed CB is simply there as a switch to interface with the mechanical interlock, and the Main CB fed from the utility company.

I have had problems getting the smaller 20A & 30A BR breakers with the hold down screw hole provision, but 50A & 60A with the hold down hole are readily available
 
Last edited: