Why is there instantaneous in the first place when it seems like thermal curves coordinate but magnetic ones can overlap?
In older breakers you can buy just the trip functions you needed. Like just LS or LSG instead of say LSIG. But in modern microprocessor breakers it’s all the same cost so no reason not to offer one trip unit that does everything.
Yes and Yes, but none of this explains why instantaneous trip is added to feeder breakers or why it can be over ridden.
But why do some (most) not give you the option of disabling it?
I hear you, but I was told the instantaneous was/is necessary according to some UL standard.
Generally you will only find the ability to turn off the instantaneous on UL 1066 Low Voltage Power Circuit Breakers installed in UL 1558 Switchgear because it has a 30 cycle short circuit rating.
A breaker feeding equipment that only has a 3 cycle short circuit rating, like UL 891 Switchboard, needs the instantaneous turned on to protect it past 3 electrical cycles.
I assume a fault over 30 cycles would put you into the short time rating.
A breaker feeding equipment that only has a 3 cycle short circuit rating, like UL 891 Switchboard, needs the instantaneous turned on to protect it past 3 electrical cycles.
You can get UL489 breakers, installed in UL891 equipment, which have selectable Instantaneous settings including OFF. When the Inst function is turned off, there will still be an integral 'self-protection', or override, point to comply with the 3 cycle issue. The override has not traditionally been shown on breaker TCCs, although it seems more manufacturers are beginning to make note of it because it needs to be considered for selective coordination.
Though it might not, depends on the run and source Z.