Just my opinion but the wire size for a single motor is sized using motor table of article 430. To get the FLC and then 430.22(A) tells me to multiply the FLC from the motor tables by 125%.
EX: 10hp 3 phase 208V = 30.8 FLC
Applying 430.22 30.8 x 1.25 = 38.5 Ampacity
Looking at table 310.16
38.5 Ampacity lets round up to 40 amps (220.5(B))
and we will assume "THHN" and equipment rated at 75 degrees. 40 amps Ampacity = 8 AWG THHN
And for the OCD if you are using Inverse time breakers. 38.5 x 250% = 96.25 Amps. 240.6 tells me I can use a 100 amp breaker. Article 240.4(D) does not apply to motor circuits. Lets see what others have to say, I am just an apprentice.......