I posted a similar thread before regarding power breaker withstand ratings but it is now closed so I wanted to re-visit this topic again.
I understand that a typical power breaker has both an Interrupting Capacity (usually couple of cycles) and withstand capacity (usually 30 cycles). In looking at a typical power breaker I see that it has a IC of 65kA and a Withstand Or Short time capacity of 50kA (I assume Withstand and Short Time are more or less refer to the same thing). So I understand these ratings to mean that the breaker can interrupt a fault up to 65kA and tolerate this fault for the couple of cycles that it takes to open the breaker and clear the fault. If a breaker does not clear the fault within the first few cycles (Instantaneous) then the rating implies that the breaker can tolerate a fault up to 50kA for 30 cycles until the short time element clears the breaker. This would be a case where the Instantaneous setting was turned off, or was above the maximum fault current so it didn't pickup and thus the fault would need to be cleared by the breakers short time.
For instance lets say that with the breaker ratings above the INST setting is turned off but the fault current available at the breaker is 53kA. In this case since the INST would not open the breaker, the breaker would need to withstand this fault current for 30 cycles until the short time element picked up. However in this case the 53kA fault current is above the withstand rating of the breaker so I'm guessing that the breaker would fail or receive a failed rating in an evaluation. In this case the INST setting could not be turned off on the breaker. Am I on the right track here?
This same case seems like it would apply to a situation where the breakers INST setting is turned off, or set above the maximum fault current for coordination purposes. In either of these cases the engineer must then look at the maximum fault current to determine weather or not the breaker can withstand the maximum for 30 cycles. Is this correct? I'm not sure how plausible the example that I gave above is but I guess it could happen.
I also believe that equipment such as MCC's and Switchboards have similar withstand ratings? In other words an MCC has a 3 cycle and 30 cycle rating? Is this also a consideration when turning off the INST setting on a feeder breaker?
I understand that a typical power breaker has both an Interrupting Capacity (usually couple of cycles) and withstand capacity (usually 30 cycles). In looking at a typical power breaker I see that it has a IC of 65kA and a Withstand Or Short time capacity of 50kA (I assume Withstand and Short Time are more or less refer to the same thing). So I understand these ratings to mean that the breaker can interrupt a fault up to 65kA and tolerate this fault for the couple of cycles that it takes to open the breaker and clear the fault. If a breaker does not clear the fault within the first few cycles (Instantaneous) then the rating implies that the breaker can tolerate a fault up to 50kA for 30 cycles until the short time element clears the breaker. This would be a case where the Instantaneous setting was turned off, or was above the maximum fault current so it didn't pickup and thus the fault would need to be cleared by the breakers short time.
For instance lets say that with the breaker ratings above the INST setting is turned off but the fault current available at the breaker is 53kA. In this case since the INST would not open the breaker, the breaker would need to withstand this fault current for 30 cycles until the short time element picked up. However in this case the 53kA fault current is above the withstand rating of the breaker so I'm guessing that the breaker would fail or receive a failed rating in an evaluation. In this case the INST setting could not be turned off on the breaker. Am I on the right track here?
This same case seems like it would apply to a situation where the breakers INST setting is turned off, or set above the maximum fault current for coordination purposes. In either of these cases the engineer must then look at the maximum fault current to determine weather or not the breaker can withstand the maximum for 30 cycles. Is this correct? I'm not sure how plausible the example that I gave above is but I guess it could happen.
I also believe that equipment such as MCC's and Switchboards have similar withstand ratings? In other words an MCC has a 3 cycle and 30 cycle rating? Is this also a consideration when turning off the INST setting on a feeder breaker?