Breaker and wire size for ductless mini split?
natesc0tt
New User
San Diego, CA
Electrical Engineer
installing this mini split:
CH-12MSPHCT-230VI
12000BTU
21.5 Seer
1 Ton
Max Fuse: 15A
it says, connecting wire: 16AWG/4
power supply wire: 14AWG/4
I would feel better with 12gauge and a 20A breaker instead of 14gauge/15A. I don't think that's overkill for an AC system even this is relatively smaller system.
thoughts?...
You can't provide 20A overcurrent protection if the maximum is listed as 15A.
No problem using 20gauge wiring.
CH-12MSPHCT-230VI
12000BTU
21.5 Seer
1 Ton
Max Fuse: 15A
thoughts?...
The actual draw on a unit like that is about 7 amps. You would feel better putting a breaker on it that might not trip?
nates: So as not to confuse your situation, we were making light of david's typo for a #20 wire. The manufacturer requirement for a 15 amp fuse takes precedent so you must have a 15 amp fuse in the circuit. You can install a #14 or #12 wire (or larger)
This site is designed for:
  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.
To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.