Re: breaker and wire sizes
This may help
You did not indicate the horsepower rating of the two motors but lets say the first is a 5 HP 3 phase 208-induction motor.
Art 430.6A for general motors requires that the entire motor branch circuit (except the running protection) be sized based upon the tables FLA. Table 430.150 lists a 5HP motor with a FLA of 16.7A. I will use that as an example.
430.22 requires the motor branch circuit conductors have an ampacity not less than 125% of the tables FLA 1.25 X 16.7 = 20.875A.
Table 310.16 lists a #12 Cu 75 deg C copper wire with an ampacity of 25A.
This conductor is appropriate for the conditions of 430.22
430.52 States the Branch Circuit and Short Circuit and Ground Fault Protection may be sized as follows
Time Delay 175% of 16.7 = 29.2A select 30A Fuse
Non Time Delay 300% of 16.7 = 50.1A select 50A Fuse
Inverse Trip Breakers 250% of 16.7 = 41.75 select 50A (45A) Fuse
The section allows the next higher sizes OCPD if the calculation does not coincide with those listed in 240.6. That can be tricky and it was debated in the 93 code.
240.4 (G) recognizes several applications in the Code, which can allow small conductors (240.4 (D)) to be protected at ampacities exceeding the general 15, 20, and 30A limitations.
That 12-gage conductor may have short circuit and ground fault protection set as indicated above. Theses devices are set higher to allow the motors to start. They protect the circuit from high current faults. Note that this is short circuit protection.
As Don mentioned the conductors must be protected at their ampacity. 430.6 A requires the running protection to be set per 430.31 and 32, 125% or 115% of the NAME PLATE CURRENT (generally). For example if the running protection for this motor is set at 125% of 16.7 it would protect the entire branch circuit at a level of 20.875 A. the conductor has an ampacity of 25A.
Motor circuit protection is a coordinated effort between the fuse or breaker and the overload device. The code understands and recognizes this. This is a long time practice and it works fine and lasts a long time.
Hope this helps
charlie
I edited the inverse trip breaker to 45 A as noted in the folowing post by Roger thanks again