"Home Inspectors" (increasingtly being used before contract closings on house sales, not to be confused with Code Enforcement Inspectors and Electrical Inspectors such as the NYBFU) are tending to automatically take sensationalized internet comments and then reporting such as an immediate alarm condition -- bad rap breakers being deal breakers, for example.
I have been able to confirm that UL has not retracted its listings remaining on currently-installed old FPE boxes and breakers. This is not because UL does not ever retract its listings -- it has for some "really bad players" for a wide variety of products. However, I have also been able to confirm that some old FPE breakers were not made so that their operation would be as reliable as we should expect on over-current protection devices.
Newer technology breakers have been made (and some continue to be sold by Home Depot -- at least online at homedepot.com) that fit and work in FPE panels. Some appear to be NOS never-been-used while others are described as "refurbished." As I understand, UL does not test or list refurbished equipment, and that a used breaker, although perhaps still carrying a UL marking, may no longer be -- and likely is not -- as reliable as new (who knows where it's been and whats it's done in earlier incarnations).
So, based on my understanding at this point, as I have tried to outline above, I have a question:
How do those of you who have dispassionate views on the FPE breaker issue feel about a retrofit of NOS UL-listed non-FPE breakers being installed in an old FPE panel to directly replace all of the FPE-made breakers?
That is, if an existing installed FPE load center had all of the older FPE-made breakers removed (especially the 240-volt 2-pole breakers that some websites claim do not trip with a line-to-neutral fault) and then retrofit with New-Old-Stock American Breaker breakers that were made to fit directly into the FPE panels, would the load center then be as reliable as we should expect for current-overload protection?
Thank you for any and all comments.
I have been able to confirm that UL has not retracted its listings remaining on currently-installed old FPE boxes and breakers. This is not because UL does not ever retract its listings -- it has for some "really bad players" for a wide variety of products. However, I have also been able to confirm that some old FPE breakers were not made so that their operation would be as reliable as we should expect on over-current protection devices.
Newer technology breakers have been made (and some continue to be sold by Home Depot -- at least online at homedepot.com) that fit and work in FPE panels. Some appear to be NOS never-been-used while others are described as "refurbished." As I understand, UL does not test or list refurbished equipment, and that a used breaker, although perhaps still carrying a UL marking, may no longer be -- and likely is not -- as reliable as new (who knows where it's been and whats it's done in earlier incarnations).
So, based on my understanding at this point, as I have tried to outline above, I have a question:
How do those of you who have dispassionate views on the FPE breaker issue feel about a retrofit of NOS UL-listed non-FPE breakers being installed in an old FPE panel to directly replace all of the FPE-made breakers?
That is, if an existing installed FPE load center had all of the older FPE-made breakers removed (especially the 240-volt 2-pole breakers that some websites claim do not trip with a line-to-neutral fault) and then retrofit with New-Old-Stock American Breaker breakers that were made to fit directly into the FPE panels, would the load center then be as reliable as we should expect for current-overload protection?
Thank you for any and all comments.