This is a puzzler to me...
A solar system of ours wasn't working because the inverters were not seeing the correct voltage (240V nominal). We sent a guy out and he measured at the terminals of the breaker. One leg was 120V to ground and the other was 80V to ground. L-L voltage was under 200. Voltage in the rest of the panelboard was fine, so he replaced the breaker, and all was well.
Also, inverters had a data connection through the good leg and they record around 25V L-L before the breaker was fixed.
Okay, bad breaker, problem solved. But I want to understand how a voltage drop could show up with no load in this situation, and why the inverters would record a different voltage than a Fluke. Any thoughts?
A solar system of ours wasn't working because the inverters were not seeing the correct voltage (240V nominal). We sent a guy out and he measured at the terminals of the breaker. One leg was 120V to ground and the other was 80V to ground. L-L voltage was under 200. Voltage in the rest of the panelboard was fine, so he replaced the breaker, and all was well.
Also, inverters had a data connection through the good leg and they record around 25V L-L before the breaker was fixed.
Okay, bad breaker, problem solved. But I want to understand how a voltage drop could show up with no load in this situation, and why the inverters would record a different voltage than a Fluke. Any thoughts?