I have a 2500 amp main, a 800 amp feed to a mcc from switch board, and 500 amp inverse time breaker bucket feeding a 200 hp motor. These are all in series with each other out to the motor. Recently we have a lightning storm I had to come in because the main had tripped upon further investigation the 800 amp feeder and the 200hp bucket had also tripped all at the same time. My first question is can lightning create a surge tripping everything downstream of the device it struck?
My second question is this motor is has very high iduction and the inrush from the chart my plc graphs based on the PLC shows when we tried to start the motor back up we were drawing almost 800 amps. Long story short when operators tried to restart the motor the main, mdp and bucket tripped again simultaneously. Why do they trip simultaneously? If it gets to the main and the main clears because they are not coordinated properly why would the mcc feed and the bucket also trip?
(I adjusted the instantaneous trip settings the second time we tried again and it started up but the windings were warm and it only drew 650 amps starting up and then leveled off to 150 and stayed level and is now working but if anyone has some insight I would appreciate any feedback)
My second question is this motor is has very high iduction and the inrush from the chart my plc graphs based on the PLC shows when we tried to start the motor back up we were drawing almost 800 amps. Long story short when operators tried to restart the motor the main, mdp and bucket tripped again simultaneously. Why do they trip simultaneously? If it gets to the main and the main clears because they are not coordinated properly why would the mcc feed and the bucket also trip?
(I adjusted the instantaneous trip settings the second time we tried again and it started up but the windings were warm and it only drew 650 amps starting up and then leveled off to 150 and stayed level and is now working but if anyone has some insight I would appreciate any feedback)