Where might I find a breaker cross reference?
Where might I find a breaker cross reference?
To expand on what others have said, You need to use a breaker that is UL listed (or classified) for use in the panel you are working on.
You can not use a Siemens Q120 breaker in a SQD Homeline panel they may fit / plug in, but you are breaking the UL listing.
We often find wrong breakers in panels, often times the buss bar is heated because the breakers from the wrong manufacturer were not designed with the same clamping pressure for the thickness of the buss in the others panel.
General rule of thumb: If it's Siemens use Siemens, if it's Homeline use Homeline, if it's GE use GE, you get the idea:happyyes:
PS: Cutler Hammer makes a line of UL classified breakers that will fit + are approved for use, in several other manufacturers panels. Check with your local Cutler Hammer distributor for sizes and information on what panels they are approved for.