jlg
Member
- Location
- crossville, tn usa
Hi, I'm looking for a little input on a situation I have. I'm trying to update all our arc flash info/labeling and came across a situation I'm a little unsure about. I have a 200A breaker with a fault clearing time of 0.025s that is feeding a 112.5kVA transformer (480 to 120/208) with a 4.8%Z that goes to a fused disconnect with 150A RK5 fuses. Am I correct in my thinking that the fuse is going to dictate my arc flash rating. The slow acting fuse is greatly increasing the arc rating to beyond CAT 4, where if the breaker was controlling it looks like it would take it down to a CAT 1. Thanks!