Re: breaker for 6 amp well pump
Thanks for your responses.
The cable from the main panel is BX to the junction box . The cable to the well casing is NM.
Since the continuous load is 6 amps then the 14/2
wire, I take it, is OK. However are you telling me that since NEC allows 250% for the breaker, then it should not, in this case, exceed 15 amps?
Suppose the rated current were 8 amps; would this then mean that the 20 amp breaker would be appropriate?