Using T430.250 for a FLA of 40A and T403.52 for a max of 250%, the breaker would be a max size of 100A for a standard inverse time breaker.
I appreciate the answer. If I were to use a breaker with magnetic trips would the 100a be the same? I assume thE wire size wouldn't handle that higher amperage breaker if something happened to wiring. Thanks again.
I appreciate the answer. If I were to use a breaker with magnetic trips would the 100a be the same? I always assume thE wire size wouldn't handle that higher amperage breaker if something happened to wiring which is why I lack confidence with breaker being larger thaN wire Thanks again.
You can’t use a mag-only breaker on your own anyway, they can only be used as part of a listed assembly like a combo motor starter. In that case, the OL relay protects the wires, so the mag-only breaker can be whatever size is needed to get the mag trips that follow the applicable rules.
Is the motor the only thing on this feeder? If so, the same rules apply.
You need a breaker at the supply end of the conductors and you need a disconnect within sight from the motor controller (starter). In some cases the breaker at the panel can satisfy both requirements.Yes only thing on feeder. What I need 2 breaker one for feeder and one for starter?
You need a breaker at the supply end of the conductors and you need a disconnect within sight from the motor controller (starter). In some cases the breaker at the panel can satisfy both requirements.
You need a breaker at the supply end of the conductors and you need a disconnect within sight from the motor controller (starter). In some cases the breaker at the panel can satisfy both requirements.
You don't use any kind of special breaker. Just a standard thermal magnetic breaker at the supply end of the conductors that feed the motor controller.The real problem as to why so may questions about motors. I need a 100a breaker. The panel is 1200a siemens 480 3p panel. The current installation has fuses for motor controller. The customer wants a breaker not fuses. Siemens doesn't make 100a for motor protection and no one carries 100a only 150a . The 150a in Odessa Tx is $3600. Per our conversation I need 2. Thats my situation. If you guys have any suggestions please let me know.
If you have a feeder breaker in the switchboard that is feeding nothing but that motor starter, you do not need another breaker or fuses at the motor starter, but you may need a disconnect switch. But non-fused disconnects have very low SCCR values, ie 10kA, and most industrial applications will have more than that available. Since you cannot retrofit with an MCP (legally), a Thermal-mag Breaker would be easier.