Originally posted by pierre:
Bob
If you read the complete text of 240.20(B)(1), (2), & (3) The use of 'approved handle ties' is part of the text.
Hi Pierre, Maybe I did not explain myself well, here is what I said earlier with some bolding.
Quote by me
240.20(B) requires the breaker to open all ungrounded conductors unless allowed by 240.20(B)(1) or (2) or (3)
And for comparison the actual code text.
240.20(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit unless otherwise permitted in 240.20(B)(1), (B)(2), and (B)(3).
There is no reference to handle ties in 240.20(B), it says circuit breakers shall open all ungrounded conductors of the circuit, not circuit breakers with handle ties.
To me this leaves internal trip breakers as the only way to comply with 240.20(B) itself.
Big Johns question was about a feeder that serves line to neutral loads so only 240.20(B) is relevant, he does not meet the criteria of parts 1, 2, or 3
Big Johns circuit was not a Multiwire Branch Circuit so 240.20(B)(1) is not relevant
Big Johns circuit is closest to meeting the requirements of 240.20(B)(2) Single-Phase and 3-wire dc Circuits. If he did meet all the requirements of this section handle ties would clearly be allowed.
240.20(B)(2)
(2) Grounded Single-Phase and 3-wire dc Circuits. In grounded systems, individual single-pole circuit breakers with approved handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.
Big Johns circuit is certainly grounded single phase but it does not serve line to line loads
His circuit as described serves line to neutral loads, so IMO that makes 240.20(B)(2) irrelevant in this case.
240.(B)(3) 3-Phase and 2-Phase Systems, is also not relevant in Big Johns circuit.
Bob