breaker height rule

Status
Not open for further replies.

stew

Senior Member
I was under the impression that on a service panel as long as the main breaker was under the height of 6 7 then you were ok. Is this correct or not? Or do ALL the branch breakers have to be under 6-7 I always thoght that exception 3 on 220.24 allowed it with reference to 225.4. But I guess that the main breaker is not considered a feeder breaker eh? Hope this isnt a dumb question.
 

bphgravity

Senior Member
Location
Florida
Re: breaker height rule

404.8(A) and 240.24 indicate that All the overcurrent devices, switches or circuit breakers have the height limitation described in those sections.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: breaker height rule

Apparently, the reasoning is that excessive height (different for different people, obviously) renders breakers less than 'readily accessible'.
 
Re: breaker height rule

Art,404.8 - ALL SWITCHES & CIRCUIT BREAKERS used as switches shall be located so that they may be operated from a readily accessible place.
 

allenwayne

Senior Member
Re: breaker height rule

Most poco`s around here require The meter to be set at 5 1/2 ft above grade to center line.In order too meet the 6 7 would be a pain to maintain.
The inspectors let it go on back to hack services,or you can use the upper factory ko,which leaves the top bkr, well it is lower than the 6 7 rulling,while :D the rest of breakers are way lower the panel max :D
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: breaker height rule

Originally posted by allenwayne:
Most poco`s around here require The meter to be set at 5 1/2 ft above grade to center line.In order too meet the 6 7 would be a pain to maintain.
Yeah it's a good thing we can ignore the rules when they are "a pain" to follow. :roll:

[ September 04, 2005, 05:40 AM: Message edited by: iwire ]
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Re: breaker height rule

Bob,
Isn't that listed right below the rule that NEC requirements can be altered dependant on truck inventory?
"I knew the Code called for a #10 ground, but #12 green was all I had on the truck" :p
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: breaker height rule

Originally posted by augie47:
Bob,
Isn't that listed right below the rule that NEC requirements can be altered dependant on truck inventory?
Yeah that would be also near the exception for reduced burial depths if the digging is hard or if it's really hot out. :D
 

pierre

Senior Member
Re: breaker height rule

"Yeah that would be also near the exception for reduced burial depths if the digging is hard or if it's really hot out."

You missed, " but that cost more money"

Seriously, you may be surprised how often an inspector hears these kind of excuses - they probably worked when these guys were in school.

Oh yeah, my dog ate the plans :D
 

luckyshadow

Senior Member
Location
Maryland
Re: breaker height rule

I had to cut the ground rod off !! There's rocks in the ground and that makes it hard to drive it in all the way, besides I got about 6 feet of in! :roll:
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: breaker height rule

The worst part of cutting a rod is making the freshly-cut end look like you've been pounding on it. :eek:
 

peter

Senior Member
Location
San Diego
Re: breaker height rule

Mr. Fine,
Not only "The worst part of cutting a rod is making the freshly-cut end look like you've been pounding on it" but the top end of a ground rod has a small cone-shaped divot in the middle of it. Imspectors look for this divot. Knowledgeable apprentices always carry a countersink with them for this situation.
~Peter :eek:
 

dillon3c

Senior Member
Re: breaker height rule

Originally posted by peter:
Knowledgeable apprentices always carry a countersink with them for this situation.

Umm,yeh..

These must be the same apprentices that use "black phase tape" on the ends of their NM Cable, before they dye it to a differant color around April Fools Day.. ;)
 

allenwayne

Senior Member
Re: breaker height rule

Originally posted by peter:
Mr. Fine,
Not only "The worst part of cutting a rod is making the freshly-cut end look like you've been pounding on it" but the top end of a ground rod has a small cone-shaped divot in the middle of it. Imspectors look for this divot. Knowledgeable apprentices always carry a countersink with them for this situation.
~Peter ;)
 