I have a 480 volt panel feeding a 75kva transformer within 10 feet. Does the secondary panel need a main breaker or can it be main lugs?
You might be thinking straight 480, not 480Y/277 240.4(F). The wye-delta needs secondary protection.Interesting that inquiry omited advising what the secondary configuration was. One would assume that it is a 480Y/277 or more commonly a 208Y/120 if in fact it was a 3ph transformer. as such secondary protection is required. If it was a 240 delta secondary it is not required as I understand the NEC requirements.
Again, the question is abbiguous in that it cold be a 1ph transforer and if so wold most likely have a 120/240 1ph3w secondary which would require secondary protection. If the secondary was 1ph2w which is somewhat uncommon then it would not.
It sould be noted that if secondary protection is not required the primary OCPD must be sized accordingly.
As a former application engineer I have become very cautious about answering ambiguous questions and questions that are asked in a way that the person who is asking the questions is trying to get an answer which they want to hear which may be the incorrect answer. I have become very gun shy.
At 480 volts / 75 kVA, it is probably not single-phase.
Interesting that inquiry omited advising what the secondary configuration was. One would assume that it is a 480Y/277 or more commonly a 208Y/120 if in fact it was a 3ph transformer. as such secondary protection is required. If it was a 240 delta secondary it is not required as I understand the NEC requirements.
Again, the question is abbiguous in that it cold be a 1ph transforer and if so wold most likely have a 120/240 1ph3w secondary which would require secondary protection. If the secondary was 1ph2w which is somewhat uncommon then it would not.
It sould be noted that if secondary protection is not required the primary OCPD must be sized accordingly.
As a former application engineer I have become very cautious about answering ambiguous questions and questions that are asked in a way that the person who is asking the questions is trying to get an answer which they want to hear which may be the incorrect answer. I have become very gun shy.
It would be very plausible to have 480V, 2-pole (single phase) breaker feeding a 75KVA single phase transformer stepping the voltage down to 120/240V.
Not enough info in the OP to answer question as stated.
There's certainly enough information in the OP to answer the question. Whether the transformer is single phase or three phase is irrelevant to the question as stated.
The secondary panel needs either a main breaker (or fuse) or it may be a main lugs panel with a breaker (or fuse) upstream of the panel on the secondary side of the transformer, per 408.36. The single phase/three phase discussion is a MacGuffin.
The single phase/three phase discussion is a MacGuffin.
If it is single phase the primary breaker could serve all the functions of a breaker on the secondary side.
I disagree. I don't see how a c/b on the primary of a transformer could serve the function of providing overcurrent protection for a panelboard on the secondary side.
If it is single phase 2 wire, the primary breaker can function to protect the secondary conductors per 240.21(C)(1).
I disagree. I don't see how a c/b on the primary of a transformer could serve the function of providing overcurrent protection for a panelboard on the secondary side.
Can you cite a code section to back that position?
How about 240.4(F).
Can you cite a code section to back that position?