puckman
Senior Member
- Location
- ridgewood, n.j.
I thought i posted this question already, can't seem to find it.
We have 3 sq. d mhp36800 breakers listed up to 600 volts. When used at 480v 60hz they are rated for 65ka , don't know the fault clearing time. These are main breakers used in a mcc. Two are used for mains and 1 as a tie breaker.
We believe we can not work in the mcc because these cb are above the rating listed in the task tables. None of the electrical equipment has had a AF Hazard study.
Can workers switch these cb on or off ? Is the rest of the mcc off limits because of the rating of the main cb SCC ?
We have 3 sq. d mhp36800 breakers listed up to 600 volts. When used at 480v 60hz they are rated for 65ka , don't know the fault clearing time. These are main breakers used in a mcc. Two are used for mains and 1 as a tie breaker.
We believe we can not work in the mcc because these cb are above the rating listed in the task tables. None of the electrical equipment has had a AF Hazard study.
Can workers switch these cb on or off ? Is the rest of the mcc off limits because of the rating of the main cb SCC ?