This is probably a straightforward question but for some reason I keep getting confused.
I have a 2-pump motor (lift station) that has 60A breakers integrated in its front panel (1 pump is the primary, 1 is a standby). FLA=20A for 1 pump.
The OCPD rating should be 250% x FLA1 + FLA2 = 250%x20 + 20 = 70A.
Can I use an existing 100A (3-phase) circuit without replacing the 100A breaker with a 70A breaker? Since the OCPD is already installed inside the equipment.