Let me start with what I have first, then the question:
I changed an outdoor main breaker panel 200A. The panel only has the main 200A breaker and two 100A breakers, each feeding a sub panel. I put the breakers across from each other and that was the way they were installed in the panel I replaced.
This is a small office with just HVAC, receptacles and lights for the load. I would say the building is no more than 500-800 sq ft and 200A is probably overkill anyway.
The confusion I have is this. The inspector called me and said I needed to either drop one of the breakers down, or raise one up. Simply put, not to have them straight across from each other. He said that put too much load on one of the buses and would burn up one side of the bus if it wasn't moved. He said the way it was now it would be too much on one leg/bus.:?
I tried to explain that each 2-pole breaker was using both legs and no matter where I put them they would still be using both legs. It would either be A-B or B-A. Now he didn't check any loads or meter it or anything that I'm aware of.
Am I loosing my mind, because I can't get it in my head what he's talking about?
Also, if the panel is rated for 200A, wouldn't each leg be rated for 200A?
Help an old confused guy out please!:huh:
I changed an outdoor main breaker panel 200A. The panel only has the main 200A breaker and two 100A breakers, each feeding a sub panel. I put the breakers across from each other and that was the way they were installed in the panel I replaced.
This is a small office with just HVAC, receptacles and lights for the load. I would say the building is no more than 500-800 sq ft and 200A is probably overkill anyway.
The confusion I have is this. The inspector called me and said I needed to either drop one of the breakers down, or raise one up. Simply put, not to have them straight across from each other. He said that put too much load on one of the buses and would burn up one side of the bus if it wasn't moved. He said the way it was now it would be too much on one leg/bus.:?
I tried to explain that each 2-pole breaker was using both legs and no matter where I put them they would still be using both legs. It would either be A-B or B-A. Now he didn't check any loads or meter it or anything that I'm aware of.
Am I loosing my mind, because I can't get it in my head what he's talking about?
Also, if the panel is rated for 200A, wouldn't each leg be rated for 200A?
Help an old confused guy out please!:huh: