Breaker lockout kit grounding

Status
Not open for further replies.
To answer as simply as you asked, yes, as the two will be tied together where the interlock is.
 
Also a sign at the inlet is required to say what type of system is being used.

702.7(C) Power Inlet. Where a power inlet is used for a temporary connection to a portable generator, a warning sign
shall be placed near the inlet to indicate the type of derived system that the system is capable of based on the wiring of
the transfer equipment. The sign shall display one of the following warnings:
WARNING:
FOR CONNECTION OF A SEPARATELY DERIVED
(BONDED NEUTRAL) SYSTEM ONLY
or
WARNING:
FOR CONNECTION OF A NONSEPARATELY
DERIVED (FLOATING NEUTRAL) SYSTEM ONLY
 