F Fordean Senior Member Location New Jersey Occupation Electrical Contractor Mar 12, 2024 #1 Are breaker locks on 2 pole 50 amp breaker acceptable On a exterior EV charger Dont want 3r disconnect
Are breaker locks on 2 pole 50 amp breaker acceptable On a exterior EV charger Dont want 3r disconnect
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 12, 2024 #2 Breaker locks are acceptable for LOTO if LO device remains in place without lock installed. It would typically be a accessory from mfgr
Breaker locks are acceptable for LOTO if LO device remains in place without lock installed. It would typically be a accessory from mfgr
R retirede Senior Member Location Illinois Mar 13, 2024 #3 The only EVSE-specific requirement for a disconnect is in 625.43 and it’s only for equipment rated over 60A. In your case, the requirement should be no different than any other external branch circuit.
The only EVSE-specific requirement for a disconnect is in 625.43 and it’s only for equipment rated over 60A. In your case, the requirement should be no different than any other external branch circuit.