wirebender
Senior Member
- Location
- North Central Texas
Sunday, we had a customer who had a breaker catch fire and melt. This breaker is at a sewage lift station with 2- 5HP 230v 3phase grinder/pump motors. A converter supplies the high leg at around 195 volts.
I replaced the breaker and the pumps worked fine. Took some readings (true RMS) to insure no overload issues. No problems but I am not sure what the current should be in this situation as I don't work with motors or converters. The current on one motor was around 18 on one leg, 17 on another and 9 on the third. The other pump was similar 16,17 and 8. Is that you would expect?
I am going to replace the panel where the meltdown occurred tomorrow because the bus is a mess. I can take more accurate readings then as the above values are by memory.
Oh, the breaker that melted is a two pole 50A and I assume it was a breaker breakdown that caused the fire, but then I don't do a lot of service work and have never seen a breaker do this.
I replaced the breaker and the pumps worked fine. Took some readings (true RMS) to insure no overload issues. No problems but I am not sure what the current should be in this situation as I don't work with motors or converters. The current on one motor was around 18 on one leg, 17 on another and 9 on the third. The other pump was similar 16,17 and 8. Is that you would expect?
I am going to replace the panel where the meltdown occurred tomorrow because the bus is a mess. I can take more accurate readings then as the above values are by memory.
Oh, the breaker that melted is a two pole 50A and I assume it was a breaker breakdown that caused the fire, but then I don't do a lot of service work and have never seen a breaker do this.
Last edited: