mstrlucky74
- NJ
Have a panel schedule that shows the breaker for a AC unit to be "trip Amps" 40/2. The disconnect is a 2p/60a. What should I size the wire to and why? I'm thinking 2 #6 w/#8G. Thanks.
That's a good point. You must go with the LIAD information to size your conductors and fuse/CB, not the panel schedule. If someone only gave you a panel schedule and no info on the load, then you must go with the breaker size they are providing, but get it in writing that this may or may not meet code and will need to be changed, via change order, if the circuit is under sized.A fair amount of the A.C. units I have wired state in the name plate information minimum circuit ampacity/ max fuse size.
Sent from my XT1254 using Tapatalk
That's a good point. You must go with the LIAD information .
:slaphead: Should be "LOAD"LIAD?
Is that an acronym for nameplate info?
That's from my fat fingers on an iPhone screen and hitting "Submit" without checking... :dunce: