breaker panel minimum clearences

Status
Not open for further replies.

ksaltz

Member
I HAVE A SAFETY QUESTION ABOUT BREAKER PANELS ,,,WHAT IS THE MINIMUM DISTANCES IN FRONT OF AND TO THE SIDES OF THE PANEL AND PLEASE DONT REFER ME TO THAT NEC 110.26 THING :confused:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: breaker panel minimum clearences

I don't know what you are asking about because the rules that cover your question are found in 110.26 in the code book.
Don
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: breaker panel minimum clearences

I agree with Don, the rules are all there in that 110.26 thing. However think of the area around a panel for two issues:
1. Ability to access the panel with additional conduits or cables
2. Safe working space

For item its basically a large refrigerator set in front of the panel

Mike Holts Understanding the NEC has very good illustrations on 110.26
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: breaker panel minimum clearences

You need 36 inches in front, and a total of 30 inches side-to-side. The 30 inches includes the width of the panel itself. So if the panel is 24 inches wide, you need 3 more inches on each side, to get the total of 30 inches. I won?t tell you where I found these numbers.
 

ryan_618

Senior Member
Re: breaker panel minimum clearences

Charlie: With the 24" wide panelboard in your example, would it not be compliant to have 0" on one side and 6" on the other? I believe it would be, but I've been wrong before!
 
G

Guest

Guest
Re: breaker panel minimum clearences

Ryan,
I second that emotion :)

If you can put that refrigerator box in the space, you can put a panel the space, but I'm guessing Charlie B wanted to leave something for the OP to look up in 110.26 :)

[ October 30, 2003, 02:42 PM: Message edited by: awwt ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: breaker panel minimum clearences

Perhaps you have noticed, that us moderators will answer a question with the appropiate code section, with the assumption being the person asking has a code book. Sometimes we don't, its it the truck or at work, and thats OK, it happens to me once in awhile...
 