I came across the following circuit on a design that was engineered by another company:
480V Switchboard
|
175A Rated Thermal-Magnetic Circuit Breaker, Fixed LT Trip, Adjustable Instantaneous Trip
|
(1) set of #2 CU conductors in conduit, 40 feet
|
50 HP Soft Starter
|
(1) set of #2 CU conductors in conduit
|
Disconnect Switch
|
(1) set of #2 CU conductors in conduit
|
50 HP Motor
According to 2008 NEC Table 310.16, #2 CU is good for 115A if we assume 75 deg C terminations, so it would typically need to be protected by a 125A or smaller breaker. However, it is protected by a 175A breaker in this case. Is this a code violation?
Since this is a motor feeder, does Table 430.52 allow the #2 conductors to be fed from a 175A breaker in this situation?