Would I be able to load a breaker to 18A if the load was not continuous? And also are lighting circuits in commercial considered continuous load?
 
I agree an OCP can be loaded to 100% if the load is non-continuous. Commercial lighting without some sort of occupancy control is almost always a continuous load.
 