Most are either nuts on studs or tapped holes in the bus, but I think there are some that are bolts and nuts.Thank you. And how do you access to unbolt? Rear?
Thanks. I'm asking how you access the bolts/bus to unbolt? Remove cover from rear?Most are either nuts on studs or tapped holes in the bus, but I think there are some that are bolts and nuts.
Why is lockout tag out required when removing breaker? What exactly is that...i have heard of it...LOTOIf you are estimating, the coordination to shutdown the panel and do the lock out tag out, may take longer than removing the cover and unbolting a breaker.
You have to de-energize the equipment and then lock it out to prevent anyone from re-energizing the equipment while it is being worked.Why is lockout tag out required when removing breaker? What exactly is that...i have heard of it...LOTO
Have never seen one where you needed rear access.Thanks. I'm asking how you access the bolts/bus to unbolt? Remove cover from rear?
So how do you access the bus/bolts.Have never seen one where you needed rear access.
Remove the dead front.So how do you access the bus/bolts.
I always try to accurately( or as close to actual as possible) labor everything although that sometimes does not happen.
When removing a breaker like these(hashed) what is involved in getting it out? Thanks
View attachment 2579901
What's the dead front ? A blank panel?Remove the dead front.
There are a number of designs. Do you have pictures of the switchboard? If not, the make and model?What's the dead front ? A blank panel?
I called it the gut cover. Covered the breakers.What's the dead front ? A blank panel?
I'll getThere are a number of designs. Do you have pictures of the switchboard? If not, the make and model?
They equipment had a built-in overhead traveling hoist that after you used a 3/8" speed wrench to crank.out enough to open contacts you hung on a bracket to bottom of circuit breaker after you pull it all the way out. then would lower it ( or raise it if is was low to the ground ) to a cart. Was told these breakers cost more then we made in a year. Had a three to five line display that you could access volts, ampere, power factor & other items. When we performed weekly walk thru of every 13,200 & 4,160 volt switchgear room we had to record line voltage & ampere from them. A coup!e of times we had problems with the incoming utility voltage bring a little low affecting some thing like MRI'S or maybe CAT Scans.Large rich hospital & research centers that I retired from all had rack.480 volt circuit breakers in the 7 or 8 substations that were maybe 30 years old or newer. They had at least 6 spare breakers in every MDP . A company would cone in every yearbto.perform cleaning & testing on all.if them and every three years a tri annual maintenance.. Older rooms had a lot of the Square D think called I line breakers that plug in.
starting at 400 amps.
Most bolt-in breakers are accessible by removing the deadfronts. I-Line panels are a little different. There are flanges on the breakers that screw the breakers to the housing and you use a screwdriver to pry the breakers on and off the bus.Thanks. I'm asking how you access the bolts/bus to unbolt? Remove cover from rear?