Breaker Removal

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I always try to accurately( or as close to actual as possible) labor everything although that sometimes does not happen.

When removing a breaker like these(hashed) what is involved in getting it out? Thanks

1759504095406.png
 
If you are estimating, the coordination to shutdown the panel and do the lock out tag out, may take longer than removing the cover and unbolting a breaker.
 
If you are estimating, the coordination to shutdown the panel and do the lock out tag out, may take longer than removing the cover and unbolting a breaker.
Why is lockout tag out required when removing breaker? What exactly is that...i have heard of it...LOTO
 
Large rich hospital & research centers that I retired from all had rack.480 volt circuit breakers in the 7 or 8 substations that were maybe 30 years old or newer. They had at least 6 spare breakers in every MDP . A company would cone in every yearbto.perform cleaning & testing on all.if them and every three years a tri annual maintenance.. Older rooms had a lot of the Square D think called I line breakers that plug in.

I always try to accurately( or as close to actual as possible) labor everything although that sometimes does not happen.

When removing a breaker like these(hashed) what is involved in getting it out? Thanks

View attachment 2579901

starting at 400 amps.
 
Unlike loadcenters (mostly residential) where the cover is one piece, and exposes the entire interior, panel boards have two covers, one outer, when removed, exposes wiring, and breaker load side terminals, then the second cover (dead front) when removed, exposes the line side of the breakers and buss. Allows testing while limiting exposure to live parts.
 
Large rich hospital & research centers that I retired from all had rack.480 volt circuit breakers in the 7 or 8 substations that were maybe 30 years old or newer. They had at least 6 spare breakers in every MDP . A company would cone in every yearbto.perform cleaning & testing on all.if them and every three years a tri annual maintenance.. Older rooms had a lot of the Square D think called I line breakers that plug in.



starting at 400 amps.
They equipment had a built-in overhead traveling hoist that after you used a 3/8" speed wrench to crank.out enough to open contacts you hung on a bracket to bottom of circuit breaker after you pull it all the way out. then would lower it ( or raise it if is was low to the ground ) to a cart. Was told these breakers cost more then we made in a year. Had a three to five line display that you could access volts, ampere, power factor & other items. When we performed weekly walk thru of every 13,200 & 4,160 volt switchgear room we had to record line voltage & ampere from them. A coup!e of times we had problems with the incoming utility voltage bring a little low affecting some thing like MRI'S or maybe CAT Scans.
 
Thanks. I'm asking how you access the bolts/bus to unbolt? Remove cover from rear?
Most bolt-in breakers are accessible by removing the deadfronts. I-Line panels are a little different. There are flanges on the breakers that screw the breakers to the housing and you use a screwdriver to pry the breakers on and off the bus.
 
This is a switchboard and not a panelboard. (as far as I know the maximum current rating of a panelboard is 1200 amps, and this is rated 4000 amps)
A switchboard may even have draw out breakers like switchgear. However switchboards are available with both fixed and draw out breakers.
 