Could it be time overcurrent???
I've read the other answers, and think it is Timed Open ContactI have a breaker schematic here. Will someone please guide me to understand what TOC is? Thank you.
https://cdn.selinc.com/assets/Liter...s/351-5-6-7_DS_20160715.pdf?v=20160815-111713
Pg 14
IN102 'trip ckt monitor'
In202 is the trip ckt monitor.. It is connected in parallel with the trip contact..
From me, i should look at the legend.. Hihi.. It could be overcurrent or the trunk open contact.. Trunk open contact in most cases are mechanically interlocked, i normally but monitor this one.. It could overcurrent signal from other relays..
Sent from my iPad using Tapatalk
Not in the manual
IN102 trip ckt monitor
IN202 unassigned programmable input
???
is wired with Out101 shunted by IN202
I'ld like to see the rest of the ckt
The manual has nothing do the question especially if the input has been assigned to other things.
In the figure, out101 is assigned to trip.. It is clear in the diagram. To assign a trip ckt monitor, all you have to do is connect this input parallel to tripping ckt to monitor the circuit.
In202 will allow some current to pass through its coil. But this current cannot activate the main tripping coil but enough to activate the optoisolated input.
Please refer to "breaker trip circuit design" ieee report on relaying committee website.
No programming is needed in in202. If this activated it means ckt is okay ready to trip.. If not it could breaker open or something else. That the time you will create some logic for alarm or other purposes.
Sent from my iPad using Tapatalk
In102 in the diagram has been labeled cust use... Customer use... Obviously i wont refer in the manual.. It will give confusion..
Sent from my iPad using Tapatalk
No problemHaha sorry that out102... In102 is probably trunking cb
In my place, and in the installations and designs i have made.. We use this kind of setup like in202 as trip ckt monitor.. So if no power, and the breaker is closed, it will declare an alarm.. This has also been published in the ieee document similar in this situation.
Other relays like basler be1-11 series have already a coil connected in parallel to one on its output builtin to its board.
Is loss of trip power and trip ckt monitor not the same?
Sent from my iPad using Tapatalk